CSLB General Building (B) practice questions: HVAC

Section 3 of 5: Core Trades

4 free practice questions on HVAC, part of a section that is about 30% of the General Building exam. Try each one, then open the answer: every choice is explained, and the answer names the code section or public rule it comes from.

Questions and answers

  1. 1. A furnace sits 15 feet from the attic access opening. What working platform is required in front of its service side?

    Core Trades

    • A. A level platform at least 30 by 30 inches
    • B. A level platform at least 24 by 24 inches
    • C. A level platform at least 36 by 36 inches
    • D. No platform; the 24-inch walkway is enough
    Show answer

    Correct answer: A

    • A. A level platform at least 30 by 30 inches

      Correct answer

      Correct: 30 by 30 inches.

    • B. A level platform at least 24 by 24 inches

      Wrong: too small.

    • C. A level platform at least 36 by 36 inches

      Wrong: larger than required.

    • D. No platform; the 24-inch walkway is enough

      Wrong: the walkway does not replace the service platform.

    Explanation

    California Mechanical Code section 304.4.3 requires a level working platform at least 30 by 30 inches in front of the service side of the appliance. The only exception is a furnace serviceable from the access opening with its service side within 12 inches of the opening, which is not the case 15 feet away.

    Source

  2. 2. Supply and return ducts for a new home's furnace run through a vented attic. Under the Energy Code's mandatory measures, what is the minimum installed insulation level for these ducts?

    Core Trades

    • A. R-4.2
    • B. R-6.0
    • C. R-8.0
    • D. R-13
    Show answer

    Correct answer: B

    • A. R-4.2

      Wrong: R-4.2 is only for qualifying unvented attics.

    • B. R-6.0

      Correct answer

      Correct: R-6.0 minimum installed.

    • C. R-8.0

      Wrong: higher than the mandatory minimum in Section 150.0(m)1.

    • D. R-13

      Wrong: higher than the mandatory minimum in Section 150.0(m)1.

    Explanation

    Energy Code section 150.0(m)1 sets a mandatory minimum installed level of R-6.0 for supply-air and return-air ducts and plenums. The R-4.2 alternative is limited to certain unvented attics, and verified ducts entirely in conditioned space need none, so ducts in a vented attic get R-6.0. The prescriptive or performance compliance path chosen for the house can call for more, but it cannot go below this mandatory floor.

  3. 3. A domestic dryer exhaust duct will need four 90-degree elbows. With no manufacturer allowance and no power ventilator, what is its maximum total length?

    Core Trades

    • A. 6 feet
    • B. 8 feet
    • C. 10 feet
    • D. 12 feet
    Show answer

    Correct answer: C

    • A. 6 feet

      Wrong: deducts 8 feet.

    • B. 8 feet

      Wrong: deducts 6 feet (2 feet for every elbow after the first).

    • C. 10 feet

      Correct answer

      Correct: 14 ft - (2 extra elbows x 2 ft) = 10 ft.

    • D. 12 feet

      Wrong: deducts for only one extra elbow.

    Explanation

    California Mechanical Code section 504.4.2.1 allows 14 feet including two 90-degree elbows and deducts 2 feet for each 90-degree elbow beyond two. Two extra elbows x 2 feet = 4 feet; 14 - 4 = 10 feet.

  4. 4. A new home's central forced-air furnace and air conditioner supply air through 40 feet of ductwork. What minimum air filter efficiency does the Energy Code require?

    Core Trades

    • A. MERV 6
    • B. MERV 8
    • C. MERV 11
    • D. MERV 13
    Show answer

    Correct answer: D

    • A. MERV 6

      Wrong: below the required rating.

    • B. MERV 8

      Wrong: below the required rating.

    • C. MERV 11

      Wrong: below the required rating.

    • D. MERV 13

      Correct answer

      Correct: MERV 13 or greater.

    Explanation

    Energy Code section 150.0(m)12 requires space-conditioning systems that supply air through more than 10 feet of ductwork to have filters rated MERV 13 or better, with filter racks or grilles gasketed or sealed so air cannot bypass the filter. Evaporative coolers are excepted.

Keep studying

Read the Section 3 study notes: Core Trades

All General Building topics

Study guides for this section

Test yourself

Try 25 free General Building practice questions from all five sections. Each answer explains the rule and names the code section it comes from. No sign-up.

See what the General Building exam covers