CSLB General Building (B) practice questions: Plumbing

Section 3 of 5: Core Trades

4 free practice questions on plumbing, part of a section that is about 30% of the General Building exam. Try each one, then open the answer: every choice is explained, and the answer names the code section or public rule it comes from.

Questions and answers

  1. 1. What liquid trap seal does the Plumbing Code require for a fixture trap?

    Core Trades

    • A. Not less than 2 inches and not more than 4 inches
    • B. Not less than 1 inch and not more than 3 inches
    • C. Not less than 2 inches and not more than 6 inches
    • D. Not less than 3 inches and not more than 5 inches
    Show answer

    Correct answer: A

    • A. Not less than 2 inches and not more than 4 inches

      Correct answer

      Correct: 2 inches minimum, 4 inches maximum.

    • B. Not less than 1 inch and not more than 3 inches

      Wrong: a 1-inch seal is too shallow.

    • C. Not less than 2 inches and not more than 6 inches

      Wrong: the maximum is 4 inches, not 6.

    • D. Not less than 3 inches and not more than 5 inches

      Wrong: the minimum is 2 inches and the maximum 4 inches.

    Explanation

    California Plumbing Code section 1005.1 requires each fixture trap to have a liquid seal of not less than 2 inches and not more than 4 inches (a deeper seal only where the Authority Having Jurisdiction requires it).

  2. 2. A gas water heater that is not listed as flammable vapor ignition resistant (FVIR) is installed in a residential garage. Its burners and ignition devices must be at least how high above the garage floor?

    Core Trades

    • A. 12 inches
    • B. 18 inches
    • C. 24 inches
    • D. 36 inches
    Show answer

    Correct answer: B

    • A. 12 inches

      Wrong: too low.

    • B. 18 inches

      Correct answer

      Correct: 18 inches above the floor.

    • C. 24 inches

      Wrong: more than the minimum.

    • D. 36 inches

      Wrong: more than the minimum.

    Explanation

    California Plumbing Code section 507.13 requires appliances in residential garages to have all heating elements, switches, burners and burner-ignition devices at least 18 inches above the floor. Listed FVIR appliances are excepted, which is why the stem says this heater is not FVIR.

  3. 3. New drain, waste and vent piping is being water tested for the rough inspection. No section may be tested with less than what head of water?

    Core Trades

    • A. 3-foot head
    • B. 5-foot head
    • C. 10-foot head
    • D. 20-foot head
    Show answer

    Correct answer: C

    • A. 3-foot head

      Wrong: too little head.

    • B. 5-foot head

      Wrong: too little head.

    • C. 10-foot head

      Correct answer

      Correct: 10-foot head minimum, held at least 15 minutes.

    • D. 20-foot head

      Wrong: more than the code minimum.

    Explanation

    California Plumbing Code section 712.2 requires that no section be tested with less than a 10-foot head of water, and the water must stay in the system for at least 15 minutes before the inspection starts.

  4. 4. Under CALGreen, what is the maximum flow rate of a single showerhead in a new home?

    Core Trades

    • A. 1.5 gallons per minute at 80 psi
    • B. 2.0 gallons per minute at 80 psi
    • C. 2.5 gallons per minute at 80 psi
    • D. 1.8 gallons per minute at 80 psi
    Show answer

    Correct answer: D

    • A. 1.5 gallons per minute at 80 psi

      Wrong: lower than the limit; not the CALGreen maximum.

    • B. 2.0 gallons per minute at 80 psi

      Wrong: higher than allowed.

    • C. 2.5 gallons per minute at 80 psi

      Wrong: higher than allowed.

    • D. 1.8 gallons per minute at 80 psi

      Correct answer

      Correct: 1.8 gallons per minute at 80 psi.

    Explanation

    CALGreen section 4.303.1.3 limits a showerhead to 1.8 gallons per minute at 80 psi, and it must be certified to the US EPA WaterSense specification. Where a shower has more than one showerhead, the combined flow from a single valve also may not exceed 1.8 gallons per minute.