CSLB General Building (B) practice questions: Insulation, acoustical, and weatherproofing

Section 3 of 5: Core Trades

4 free practice questions on insulation, acoustical, and weatherproofing, part of a section that is about 30% of the General Building exam. Try each one, then open the answer: every choice is explained, and the answer names the code section or public rule it comes from.

Questions and answers

  1. 1. Where a vapor retarder is required in a wood-frame wall, on which side of the wall does it go?

    Core Trades

    • A. The interior side
    • B. The exterior side, behind the water-resistive barrier
    • C. Either side, at the installer's choice
    • D. Between two layers of cavity insulation
    Show answer

    Correct answer: A

    • A. The interior side

      Correct answer

      Correct: interior side of frame walls.

    • B. The exterior side, behind the water-resistive barrier

      Wrong side; the exterior side holds the water-resistive barrier, not the vapor retarder.

    • C. Either side, at the installer's choice

      The code names the interior side.

    • D. Between two layers of cavity insulation

      Not where R702.7 places it.

    Explanation

    California Residential Code section R702.7 places the required vapor retarder on the interior side of frame walls.

  2. 2. A 2,400-square-foot attic meets the conditions for the reduced 1/300 vent ratio. What is the minimum net free vent area that must be in upper vents no more than 3 feet below the ridge?

    Core Trades

    • A. 1.6 square feet
    • B. 3.2 square feet
    • C. 4.0 square feet
    • D. 8.0 square feet
    Show answer

    Correct answer: B

    • A. 1.6 square feet

      8 x 0.20: below the 40 percent minimum.

    • B. 3.2 square feet

      Correct answer

      Correct: 8 x 0.40 = 3.2 square feet.

    • C. 4.0 square feet

      8 x 0.50: the most that may be in the upper vents, not the minimum.

    • D. 8.0 square feet

      The total required vent area, not the upper share.

    Explanation

    Under California Residential Code section R806.2, the reduced ratio gives 2,400 / 300 = 8 square feet of total vent area. At least 40 percent and not more than 50 percent of that must be in upper vents no more than 3 feet below the ridge: 8 x 0.40 = 3.2 square feet minimum. The rest goes in the bottom one-third of the attic.

  3. 3. A new home has a wood-framed raised floor over a crawl space with ordinary open vents. What is the Energy Code's mandatory minimum floor insulation?

    Core Trades

    • A. R-11
    • B. R-13
    • C. R-19
    • D. R-30
    Show answer

    Correct answer: C

    • A. R-11

      Too low.

    • B. R-13

      Too low.

    • C. R-19

      Correct answer

      Correct: R-19.

    • D. R-30

      More than the mandatory minimum.

    Explanation

    California Energy Code section 150.0(d) requires raised floors over unconditioned space to have an overall U-factor of 0.037 or less, which in a wood-framed assembly may be shown by R-19 or greater insulation.

  4. 4. A new home has 2x6 exterior walls framed at 16 inches on center. Using cavity insulation to show the mandatory minimum, what R-value is required?

    Core Trades

    • A. R-13
    • B. R-15
    • C. R-19
    • D. R-21
    Show answer

    Correct answer: D

    • A. R-13

      Too low for either wall size.

    • B. R-15

      The 2x4 wall value.

    • C. R-19

      Too low for a 2x6 wall.

    • D. R-21

      Correct answer

      Correct: R-21 in a 2x6 wall at 16 inches on center.

    Explanation

    California Energy Code section 150.0(c) limits 2x6 framed walls to an overall U-factor of 0.069, which in wood framing may be shown by R-21 insulation in 2x6 assemblies at 16 inches on center. A 2x4 wall uses R-15.