Questions and answers

  1. 1. A new home needs five smoke alarms. How must they work together?

    Core Trades

    • A. They must be interconnected so one alarm sounds all of them
    • B. Each may work on its own
    • C. Only the hallway alarms must be connected
    • D. They must report to a monitoring company
    Show answer

    Correct answer: A

    • A. They must be interconnected so one alarm sounds all of them

      Correct answer

      Correct: interconnected.

    • B. Each may work on its own

      Not allowed in new construction.

    • C. Only the hallway alarms must be connected

      All required alarms must be interconnected.

    • D. They must report to a monitoring company

      Not required by R310.4.

    Explanation

    California Residential Code section R310.4 requires that where more than one smoke alarm is required in a dwelling unit, the alarms be interconnected so that activating one sounds all of them, audible in every bedroom with the doors closed.

  2. 2. Receptacles are being laid out along a long, unbroken wall of a new home's living room. Under the California Electrical Code, what is the farthest any point along the floor line of that wall may be from a receptacle?

    Core Trades

    • A. 4 feet
    • B. 6 feet
    • C. 10 feet
    • D. 12 feet
    Show answer

    Correct answer: B

    • A. 4 feet

      4 feet is the most a countertop receptacle spacing can be (24 inches each way), not the wall rule.

    • B. 6 feet

      Correct answer

      Correct: no point along the floor line more than 6 feet from a receptacle.

    • C. 10 feet

      10 feet is the hallway length that triggers a required receptacle.

    • D. 12 feet

      12 feet is the most two receptacles can be apart, not the distance from any point to a receptacle.

    Explanation

    California Electrical Code section 210.52(A)(1) requires receptacles in living rooms, bedrooms and similar dwelling rooms to be placed so that no point measured horizontally along the floor line of any wall space is more than 6 feet from a receptacle. That is why receptacles on a long wall end up no more than 12 feet apart.

  3. 3. A branch circuit is wired with 12 AWG copper conductors, and no other code rule allows larger protection for it. Under the California Electrical Code, what is the largest overcurrent device allowed?

    Core Trades

    • A. 15 amps
    • B. 25 amps
    • C. 20 amps
    • D. 30 amps
    Show answer

    Correct answer: C

    • A. 15 amps

      15 amps is the limit for 14 AWG copper (or 12 AWG aluminum).

    • B. 25 amps

      25 amps is the limit for 10 AWG aluminum, not 12 AWG copper.

    • C. 20 amps

      Correct answer

      Correct: 20 amps for 12 AWG copper.

    • D. 30 amps

      30 amps is the limit for 10 AWG copper.

    Explanation

    California Electrical Code section 240.4(D) limits overcurrent protection for small conductors: 15 amps for 14 AWG copper, 20 amps for 12 AWG copper and 30 amps for 10 AWG copper (15 amps for 12 AWG aluminum and 25 amps for 10 AWG aluminum). For 12 AWG copper the largest is 20 amps.

  4. 4. NM cable is run along the side of joists in a new house. Under the California Electrical Code, how must it be secured?

    Core Trades

    • A. At intervals of not more than 6 feet and within 12 inches of each box
    • B. At intervals of not more than 4 1/2 feet and within 24 inches of each box
    • C. At intervals of not more than 3 feet and within 8 inches of each box
    • D. At intervals of not more than 4 1/2 feet and within 12 inches of each box
    Show answer

    Correct answer: D

    • A. At intervals of not more than 6 feet and within 12 inches of each box

      6 feet is too far apart for NM cable; the limit is 4 1/2 feet.

    • B. At intervals of not more than 4 1/2 feet and within 24 inches of each box

      The interval is right, but the cable must be secured within 12 inches of each box, not 24.

    • C. At intervals of not more than 3 feet and within 8 inches of each box

      Closer than required; the rule is 4 1/2 feet and 12 inches.

    • D. At intervals of not more than 4 1/2 feet and within 12 inches of each box

      Correct answer

      Correct: every 4 1/2 feet and within 12 inches of each box.

    Explanation

    California Electrical Code section 334.30 requires nonmetallic-sheathed cable to be supported and secured by staples, listed cable ties, straps, hangers or similar fittings at intervals not exceeding 4 1/2 feet and within 12 inches of every cable entry into an enclosure such as an outlet box, junction box, cabinet or fitting.

Keep studying

Read the Section 3 study notes: Core Trades

All General Building topics

Study guides for this section

Test yourself

Try 25 free General Building practice questions from all five sections. Each answer explains the rule and names the code section it comes from. No sign-up.

See what the General Building exam covers