Skip to content
CalContractorPrep
Menu

CSLB General Building (B) practice questions: Subfloor and wall framing

Section 2 of 5: Framing and Structural Components

4 free practice questions on subfloor and wall framing, part of a section that is about 20% of the General Building exam. Try each one, then open the answer: every choice is explained, and the answer names the code section or public rule it comes from.

Questions and answers

  1. 1. An electrician wants to notch a 2x4 stud in an exterior wall. No stud shoe will be used. What is the deepest notch allowed? (A 2x4 is 3-1/2 inches deep.)

    Framing and Structural Components

    • A. 7/8 inch
    • B. 1-3/8 inches
    • C. 1-3/4 inches
    • D. 2-1/8 inches
    Show answer

    Correct answer: A

    • A. 7/8 inch

      Correct answer

      Right: 25 percent of 3-1/2 inches is 7/8 inch.

    • B. 1-3/8 inches

      Wrong: close to 40 percent (1.4 inches), the notch limit for nonbearing partitions, not exterior walls.

    • C. 1-3/4 inches

      Wrong: that is 50 percent of the stud depth.

    • D. 2-1/8 inches

      Wrong: close to 60 percent (2.1 inches), the limit for a bored hole, not a notch.

    Explanation

    California Residential Code section R602.6 limits a cut or notch in a stud of an exterior wall or bearing partition to 25 percent of its depth. 3-1/2 inches x 0.25 = 0.875 inch, or 7/8 inch. (Nonbearing partition studs may be notched up to 40 percent.)

  2. 2. Under CALGreen, wall and floor framing may not be enclosed while the framing members are above what moisture content?

    Framing and Structural Components

    • A. 15 percent
    • B. 19 percent
    • C. 22 percent
    • D. 28 percent
    Show answer

    Correct answer: B

    • A. 15 percent

      Wrong: stricter than the code requires.

    • B. 19 percent

      Correct answer

      Right: framing may not be enclosed above 19 percent moisture content.

    • C. 22 percent

      Wrong: higher than the code allows.

    • D. 28 percent

      Wrong: higher than the code allows.

    Explanation

    California Green Building Standards Code section 4.505.3 does not allow wall and floor framing to be enclosed while it is above 19 percent moisture content. Moisture is checked with a probe-type or contact-type meter, 2 to 4 feet from the grade-stamped end, with at least three random readings.

  3. 3. A floor framed with open-web wood trusses has living space both above and below. Draftstops must divide the concealed floor space into areas of not more than:

    Framing and Structural Components

    • A. 500 square feet
    • B. 750 square feet
    • C. 1,000 square feet
    • D. 1,500 square feet
    Show answer

    Correct answer: C

    • A. 500 square feet

      Wrong: smaller than the code requires.

    • B. 750 square feet

      Wrong: smaller than the code requires.

    • C. 1,000 square feet

      Correct answer

      Right: no concealed area over 1,000 square feet.

    • D. 1,500 square feet

      Wrong: larger than the code allows.

    Explanation

    California Residential Code section R302.12 requires draftstops where there is usable space above and below a floor-ceiling assembly whose framing is open-web trusses or perforated members (or whose ceiling is suspended below the framing). The concealed space is divided into roughly equal areas of not more than 1,000 square feet, using at least 1/2-inch gypsum board or 3/8-inch wood structural panel.

  4. 4. Floor joists bear directly on a concrete foundation wall, with no joist hangers. What is the minimum bearing length at each joist end?

    Framing and Structural Components

    • A. 1 inch
    • B. 1-1/2 inches
    • C. 2 inches
    • D. 3 inches
    Show answer

    Correct answer: D

    • A. 1 inch

      Wrong: below the minimum for any support.

    • B. 1-1/2 inches

      Wrong: 1-1/2 inches is the minimum on wood or metal, not concrete.

    • C. 2 inches

      Wrong: not the code minimum.

    • D. 3 inches

      Correct answer

      Right: at least 3 inches of bearing on masonry or concrete.

    Explanation

    California Residential Code section R502.6: each joist, beam or girder end needs at least 3 inches of bearing on masonry or concrete and at least 1-1/2 inches on wood or metal, unless approved joist hangers carry it.

Keep studying

Read the Section 2 study notes: Framing and Structural Components

All General Building topics

Study guides for this section

Test yourself

Try 25 free General Building practice questions from all five sections. Each answer explains the rule and names the code section it comes from. No sign-up.

See what the General Building exam covers