CSLB General Building (B) practice questions: Plaster, drywall, and ceilings
Section 4 of 5: Finish Trades
4 free practice questions on plaster, drywall, and ceilings, part of a section that is about 20% of the General Building exam. Try each one, then open the answer: every choice is explained, and the answer names the code section or public rule it comes from.
Questions and answers
1. A storage closet with a door is built in the enclosed space under a house stairway. What protection does the California Residential Code require inside that closet?
Finish Trades
- AA. 1/2-inch gypsum board on the walls, the underside of the stair and any soffits, on the enclosed side
- BB. 5/8-inch Type X gypsum board on both sides of the walls
- CC. No protection, because the closet is inside a single-family dwelling
- DD. 3/8-inch plywood on the underside of the stair only
Show answerHide answer
Correct answer: A
- A
A. 1/2-inch gypsum board on the walls, the underside of the stair and any soffits, on the enclosed side
✓ Correct answer
Correct: R302.7 requires 1/2-inch gypsum board on the walls, stair underside and soffits on the enclosed side.
- B
B. 5/8-inch Type X gypsum board on both sides of the walls
Wrong: R302.7 calls for 1/2-inch gypsum board on the enclosed side, not Type X on both sides.
- C
C. No protection, because the closet is inside a single-family dwelling
Wrong: R302.7 applies to dwellings; an enclosed space reached by a door needs protection.
- D
D. 3/8-inch plywood on the underside of the stair only
Wrong: plywood is not the required material, and the walls and soffits must be covered too.
Explanation
California Residential Code section R302.7 applies when the space under a stair is closed in and reached through a door or access panel: inside that space, the walls, the underside of the stair and any soffits get 1/2-inch gypsum board.
Source
2025 California Residential Code §R302.7 — Under-stair protection
2. What is the maximum framing spacing allowed for a single layer of 3/8-inch gypsum board under the California Residential Code?
Finish Trades
- AA. 12 inches on center
- BB. 16 inches on center
- CC. 19.2 inches on center
- DD. 24 inches on center
Show answerHide answer
Correct answer: B
- A
A. 12 inches on center
Wrong: 12 inches is tighter than the code limit; it is not the maximum.
- B
B. 16 inches on center
✓ Correct answer
Correct: 3/8-inch board is limited to framing at 16 inches on center.
- C
C. 19.2 inches on center
Wrong: 19.2 inches exceeds the 16-inch limit for 3/8-inch board.
- D
D. 24 inches on center
Wrong: a single layer on 24-inch framing must be at least 1/2-inch board, and on ceilings it must run perpendicular.
Explanation
California Residential Code Table R702.3.5 (section R702.3.5) limits single-layer 3/8-inch gypsum board to framing at 16 inches on center, on walls and ceilings. On ceilings it must also run perpendicular to the framing. (The table allows two layers of 3/8-inch board on 24-inch wall framing only when the face layer is installed with adhesive.)
Source
2025 California Residential Code §R702.3.5 — Application
3. Walls framed with studs at 16 inches on center get 1/2-inch gypsum board with screws and no adhesive. What is the maximum screw spacing on the wall?
Finish Trades
- AA. 8 inches
- BB. 12 inches
- CC. 16 inches
- DD. 24 inches
Show answerHide answer
Correct answer: C
- A
A. 8 inches
Wrong: 8 inches is the nail spacing for 1/2-inch board on walls.
- B
B. 12 inches
Wrong: 12 inches is the screw spacing when the wall framing is 24 inches on center.
- C
C. 16 inches
✓ Correct answer
Correct: Table R702.3.5 allows screws at 16 inches on walls framed at 16 inches on center.
- D
D. 24 inches
Wrong: 24 inches is a screw spacing allowed only with adhesive, not for board fastened without adhesive.
Explanation
California Residential Code Table R702.3.5 (section R702.3.5) allows screws at up to 16 inches on center for 1/2-inch gypsum board on walls framed at 16 inches on center without adhesive. On walls framed at 24 inches on center the screw spacing drops to 12 inches; nails are limited to 8 inches in both cases.
Source
2025 California Residential Code §R702.3.5 — Application
4. What is the minimum finished thickness of interior cement plaster applied over wire lath, measured from the face of the support?
Finish Trades
- AA. 1/2 inch
- BB. 5/8 inch
- CC. 7/8 inch
- DD. 3/4 inch
Show answerHide answer
Correct answer: D
- A
A. 1/2 inch
Wrong: 1/2 inch is the minimum for plaster applied over masonry walls.
- B
B. 5/8 inch
Wrong: 5/8 inch is the minimum for gypsum plaster over wire lath, not cement plaster.
- C
C. 7/8 inch
Wrong: 7/8 inch is the minimum for exterior cement plaster over wire lath.
- D
D. 3/4 inch
✓ Correct answer
Correct: interior cement plaster over wire lath is at least 3/4 inch thick.
Explanation
California Residential Code Table R702.1(1) (section R702.1) sets the minimum finished thickness of cement plaster over wire lath at 3/4 inch on interiors and 7/8 inch on exteriors, measured from the face of the support or backing.
Source
2025 California Residential Code §R702.1 — General
Keep studying
Test yourself
Try 25 free General Building practice questions from all five sections. Each answer explains the rule and names the code section it comes from. No sign-up.