CSLB General Building (B) practice questions: Field inspection performance
Section 1 of 5: Planning and Estimating
4 free practice questions on field inspection performance, part of a section that is about 15% of the General Building exam. Try each one, then open the answer: every choice is explained, and the answer names the code section or public rule it comes from.
Questions and answers
1. On a new raised-floor house, the inspector looks into the crawl space and finds grass, weeds and roots on the ground. Under the California Residential Code, what is required for the under-floor grade?
Planning and Estimating
- AA. It must be cleaned of all vegetation and organic material
- BB. The vegetation may stay if a vapor retarder is laid over it
- CC. The vegetation may stay if the crawl space is vented
- DD. Only vegetation within 18 inches of the floor joists must be removed
Show answerHide answer
Correct answer: A
- A
A. It must be cleaned of all vegetation and organic material
✓ Correct answer
Correct: all vegetation and organic material comes out of the under-floor grade (R408.5).
- B
B. The vegetation may stay if a vapor retarder is laid over it
Wrong: a vapor retarder does not replace removing the vegetation.
- C
C. The vegetation may stay if the crawl space is vented
Wrong: venting the crawl space does not replace removing the vegetation.
- D
D. Only vegetation within 18 inches of the floor joists must be removed
Wrong: 18 inches is the R304.1 distance from exposed ground inside which floor joists must be naturally durable or preservative-treated wood, not a vegetation rule; all vegetation must go.
Explanation
California Residential Code section R408.5 (Removal of debris) requires the under-floor grade to be cleaned of all vegetation and organic material. Covering it or venting the crawl space does not replace the cleaning, and there is no height allowance for vegetation left in place.
Source
2025 California Residential Code §R408.5 — Removal of debris
2. The ducts in a new single-family house are leak tested at rough-in, before the air handler is installed. Under the California Energy Code, total duct leakage may not exceed what share of the air handler airflow?
Planning and Estimating
- AA. 3 percent
- BB. 4 percent
- CC. 5 percent
- DD. 8 percent
Show answerHide answer
Correct answer: B
- A
A. 3 percent
Wrong: tighter than the code requires.
- B
B. 4 percent
✓ Correct answer
Correct: 4 percent at rough-in when the air handler is not yet installed (CEnC 150.0(m)11).
- C
C. 5 percent
Wrong: 5 percent is the limit when the air handler is installed and connected.
- D
D. 8 percent
Wrong: more leakage than the code allows.
Explanation
California Energy Code section 150.0(m)11 requires forced-air duct systems to be sealed and confirmed by field verification and diagnostic testing. For single-family dwellings and townhouses tested at rough-in with the air handler not yet installed, total leakage may not exceed 4 percent of the air handler airflow. With the air handler installed and connected, the limit is 5 percent.
Source
2025 California Energy Code §150.0(m)11 — Duct system sealing and leakage testing
3. The frame inspection on a house is scheduled for Thursday. The drywall crew is free on Wednesday. Under the California Residential Code, what should the contractor do?
Planning and Estimating
- AA. Hang the drywall Wednesday; the inspector can check the framing from the attic
- BB. Hang drywall on one side of each wall only
- CC. Wait until the frame inspection is approved before covering the framing
- DD. Hang the drywall and keep photos of the framing for the inspector
Show answerHide answer
Correct answer: C
- A
A. Hang the drywall Wednesday; the inspector can check the framing from the attic
Wrong: the framing must stay exposed until it is approved.
- B
B. Hang drywall on one side of each wall only
Wrong: covering any part of the framing goes past the inspection point.
- C
C. Wait until the frame inspection is approved before covering the framing
✓ Correct answer
Correct: no work beyond the inspection point until approval (R109.4).
- D
D. Hang the drywall and keep photos of the framing for the inspector
Wrong: photos do not replace the required approval.
Explanation
California Residential Code section R109.4 bars the contractor from carrying the work beyond each inspection point until the building official has signed off on it. Covering the framing before the frame inspection is approved goes past that point.
Source
2025 California Residential Code §R109.4 — Approval required
4. At the footing and foundation inspection for a commercial building, the foundation materials are supposed to be on the job. Which material does the California Building Code allow to be absent at the time of the inspection?
Planning and Estimating
- AA. Reinforcing steel
- BB. Form lumber for the concrete foundation
- CC. Anchor bolts
- DD. Ready-mixed concrete
Show answerHide answer
Correct answer: D
- A
A. Reinforcing steel
Wrong: required reinforcing steel must already be in place for this inspection.
- B
B. Form lumber for the concrete foundation
Wrong: for concrete foundations the required forms must already be in place.
- C
C. Anchor bolts
Wrong: foundation materials must be on the job; only ready-mixed concrete is excepted.
- D
D. Ready-mixed concrete
✓ Correct answer
Correct: ready-mixed concrete is the stated exception (CBC 110.3.1).
Explanation
California Building Code section 110.3.1 makes the footing and foundation inspection after the excavations are complete and any required reinforcing steel (and, for concrete foundations, the required forms) are in place, with the foundation materials on the job. The one listed exception is ready-mixed concrete (ASTM C94), which does not need to be on the job when the inspection is made.
Source
2025 California Building Code §110.3.1 — Footing and foundation inspection