  1. 1. A footing design assumed 3,000 psf allowable bearing on silty clay, with no soils investigation. Under the California Building Code table of presumptive load-bearing values, what may be assumed for silty clay?

    Planning and Estimating

    • A. 1,500 psf
    • B. 2,000 psf
    • C. 3,000 psf
    • D. 4,000 psf
    Show answer

    Correct answer: A

    • A. 1,500 psf

      Correct answer

      Correct: silty clay is in the 1,500 psf class.

    • B. 2,000 psf

      Wrong: 2,000 psf is for sand, silty sand, clayey sand, silty gravel and clayey gravel.

    • C. 3,000 psf

      Wrong: 3,000 psf is for sandy gravel and gravel.

    • D. 4,000 psf

      Wrong: 4,000 psf is for sedimentary and foliated rock.

    Explanation

    California Building Code section 1806.2 gives a presumptive vertical foundation pressure of 1,500 psf for clay, sandy clay, silty clay, clayey silt, silt and sandy silt. The 3,000 psf in the design is the value for sandy gravel and gravel, so the design overstates the soil.

  2. 2. A site plan for a new retail store slopes an accessible parking space and its access aisle at 1:20 (5 percent) toward a storm drain inlet. Under the California Building Code, what is wrong?

    Planning and Estimating

    • A. Nothing; 1:20 is the slope allowed for accessible walking surfaces
    • B. The parking space and its access aisle may not have slopes steeper than 1:48
    • C. Only the access aisle is limited to 1:48; the parking space itself may slope at 1:20
    • D. The slope is acceptable, but the access aisle must be set 1/2 inch lower than the space for drainage
    Show answer

    Correct answer: B

    • A. Nothing; 1:20 is the slope allowed for accessible walking surfaces

      Wrong: 1:20 is the running slope limit for walking surfaces (11B-403.3); parking spaces and access aisles are limited to 1:48.

    • B. The parking space and its access aisle may not have slopes steeper than 1:48

      Correct answer

      Correct: 11B-502.4 allows no slope steeper than 1:48 in the space or the aisle.

    • C. Only the access aisle is limited to 1:48; the parking space itself may slope at 1:20

      Wrong: 11B-502.4 applies the 1:48 limit to the parking space and the access aisle alike.

    • D. The slope is acceptable, but the access aisle must be set 1/2 inch lower than the space for drainage

      Wrong: 11B-502.4 requires the aisle at the same level as the space, with no changes in level.

    Explanation

    California Building Code section 11B-502.4 requires accessible parking spaces and their access aisles to be at the same level, with no changes in level and no slopes steeper than 1:48 (about 2 percent). A 1:20 slope is far too steep, so drainage has to be designed around the space and aisle.

  3. 3. Under the California Residential Code, a hole bored in a solid sawn floor joist must be at least how far from the top or bottom edge of the joist?

    Planning and Estimating

    • A. 1 inch
    • B. 1 1/2 inches
    • C. 2 inches
    • D. 3 inches
    Show answer

    Correct answer: C

    • A. 1 inch

      Wrong: closer than the 2-inch minimum.

    • B. 1 1/2 inches

      Wrong: closer than the 2-inch minimum.

    • C. 2 inches

      Correct answer

      Correct: R502.8.1 requires 2 inches.

    • D. 3 inches

      Wrong: more than the code minimum; not the code figure.

    Explanation

    California Residential Code section R502.8.1 requires bored holes in solid sawn joists, rafters and beams to be at least 2 inches from the top or bottom of the member, from any other hole and from any notch. The hole diameter is limited to one-third of the member depth.

  4. 4. Plans for a new family room show a flat ceiling 6 feet 10 inches above the floor. What is the minimum ceiling height the California Residential Code requires for habitable space?

    Planning and Estimating

    • A. 6 feet 4 inches
    • B. 6 feet 6 inches
    • C. 6 feet 8 inches
    • D. 7 feet
    Show answer

    Correct answer: D

    • A. 6 feet 4 inches

      Wrong: 6 feet 4 inches is the height allowed under beams and ducts in certain basements.

    • B. 6 feet 6 inches

      Wrong: not a figure in R313.1.

    • C. 6 feet 8 inches

      Wrong: 6 feet 8 inches is for bathrooms, toilet rooms and laundry rooms.

    • D. 7 feet

      Correct answer

      Correct: habitable space needs at least 7 feet.

    Explanation

    California Residential Code section R313.1 requires habitable space, hallways and the basement areas containing them to have a ceiling height of at least 7 feet, so a 6-foot 10-inch ceiling is an error. Bathrooms, toilet rooms and laundry rooms need at least 6 feet 8 inches.